corriee
2024-02-12 14:16
Last Edited 2024-09-04 15:49
To Add a?Kocos Push Meter to te System:
Add a Login account on your profile with a limited?Role where only following functionality?is enabled:
sdg.matiaan
2025-12-17 15:09
sdg.marinusvz
2026-07-02 17:56
Last Edited 2026-09-15 12:30
Please note that the values from KOCOS LIMO modems are almost generic, BUT you can still break things if you don't configure the right values to be pushed.
sdg.marinusvz
2026-09-15 12:35
Last Edited 2026-09-15 12:39
Please note, If you only want to read Totals for the meter, and interpolate the profile, you would typically just enable INST and not LP on the modem, and in PNPSCADA Advanced Meter Settings, you would just check the Totals checkbox and NOT the Profile checkbox.
sdg.marinusvz
2026-09-15 13:05
Last Edited 2026-09-15 13:11
Please note, that on the Acuvim-L meter, the profile come in as totals, so if you want to read profile for that meter in, it is probably best to set the MTYPE to ECHELON, enable to Profile checkbox in Advanced Meter Settings, and set the MAXDATE back and 're-read' the meter in Comms Monitor.
sdg.marinusvz
2026-09-15 13:19
PLEASE try to pass the same registers or energy quadrants (Active Forward, Active Reverse, Quadrant 1 Reactive, Quadrant 2 Reactive, Quadrant 3 Reactive, Quadrant 4 Reactive) into both LP and INST, so that we do not get apparent discrepancies. Also, please make sure that the Multiplier settings on the LIMO are reasonable, or at least the same, between LP and INST. When they are different, we obviously get discrepancies. Sometimes we get discrepancies already, when the timestamp on the INST appear to be too late in relation to the LP, and then the check total values appear to be too small. Unfortunately we are just meter readers, this cannot be fixed on PNPSCADA's side, you might want to actually stop sending totals for the 6 registers in INST to avoid this problem. Although, it might point to deeper problems in the modem, that we cannot fix: perhaps ALL the INST values you get are not on the correct timestamp as sent to us.
You will have to test and verify this yourself, we do not have physical access and cannot check with multi-meters and oscilloscopes ourselves.